Author Topic: Speed issues with TreeViews and AutoCAD Blocks  (Read 3639 times)
ChuckHardin
« on: February 27, 2006, 12:24:51 PM »
AutoCAD 2004 VB6 activeX control using ACAD Dockable Container
I am having some speed issues with an Outage Management app
Here is the gist of the app if some one has some ideas I will go into
more detail later.
AutoCAD dwg of all wire, poles, services, devices in the field for Distribution Electric Coop
when the control is running in AutoCAD (with a 55mb dwg) it queries a ODBC connection
to our Automated Outage system (it only takes phone calls and shows a flex grid of accounts
that are out of power)
If any accounts are out then it adds them to one of two treeviews
  (if the dispatcher has put it in a "Bucket" it goes in treeview2 if not it goes in treeview1)
  A "Bucket" is a outage that has been labled
if the keys do not exist in the treeview it adds blocks to the DWG showing where the outage is
  it queries another database to get the handle of the pole or service that is out of power and then uses
  the handle to get the insertion point for the block
this works great until 400 or more calls come in before the refresh fires (refresh fires once a minute)
They wanted to be able to toggle from Buckets to Unassigned Outages
Buckets View:
  If the root nodes expanded=False show a bucket block in the center point of the outage
  else show all the Devices and services
 Nodes per Call in Example
   BucketName
     >Device
    |    >Account that called
     >Device
Unassigned View:
  if the root nodes expanded=false do not show anything for that part of the tree
   Substation-Circuit
     >Device
     >Device
The toggle procedure is really slow when there are 400+ Outage calls
We have had as many as 3500 per day during severe ice storms
Just let me know who is intersted in helping and I will begin posting Code for whatever
you think is needed. warning the code for the whole app is pretty long.
ChuckHardin
Re: Speed issues with TreeViews and AutoCAD Blocks
« Reply #1 on: February 27, 2006, 01:28:07 PM »
Here is some of the code for updating the app. Iit is waht happens every time it refreshes.
Sub UpdateOutages()
Dim rsTemp As DAO.Recordset
Dim rsSSTemp As DAO.Recordset
Dim strSQL As String
Dim MyOutage As clsOutageLocation
Dim strDev As String
Dim ndLocation As MSComctlLib.Node
Dim ndDevice As MSComctlLib.Node
Dim ndBucket As MSComctlLib.Node
Dim intcnt As Integer
On Error GoTo Err_Control
 'STATUS Field Values and Description
 '1        Active Record(Power Is Off)
 '2        Power Restored
 '3        Call Back
 '4        No Response
 '5        Still Out of Power
 '6        Undialable
 '7        Error
 '8        Max Dial
 strSQL = "Select * from VIEW_RECORDS WHERE [STATUS] = 1 OR [STATUS] = 5 Order by [SUBSTATION],[CIRCUIT],[MAPNUM]"
 Set rsTemp = OpenRSPorche(strSQL)
 'Add Outages to the collection
 Do Until rsTemp.EOF
      Set MyOutage = New clsOutageLocation
      If IsNull(rsTemp.Fields("MAPNUM")) = False Then
           MyOutage.Location = rsTemp.Fields("MAPNUM")
           If Len(rsTemp.Fields("DEVICE")) > 10 Then
                strDev = Left(rsTemp.Fields("DEVICE"), 3) & "-" & Mid(rsTemp.Fields("DEVICE"), 4, 2) & "-" & Mid(rsTemp.Fields("DEVICE"), 6, Len(rsTemp.Fields("DEVICE")) - 5)
           Else
                strDev = IIf(rsTemp.Fields("DEVICE") = " ", "Unknown", rsTemp.Fields("DEVICE"))
           End If
           MyOutage.Device = strDev
           MyOutage.SubCir = IIf(Len(rsTemp.Fields("SUBSTATION")) = 2, rsTemp.Fields("SUBSTATION") & "-0" & rsTemp.Fields("CIRCUIT"), "0" & rsTemp.Fields("SUBSTATION") & "-0" & rsTemp.Fields("CIRCUIT"))
           If IsNull(rsTemp.Fields("BUCKET_NAME")) = False Then
                MyOutage.Bucket = rsTemp.Fields("BUCKET_NAME")
           Else
                MyOutage.Bucket = ""
           End If
           AddOutageToCollection MyOutage, colOutages
      End If
      rsTemp.MoveNext
 Loop
 'check to see if any need to be deleted
 If colOutages Is Nothing Then
      ResetBlockScale
      Timer2.Enabled = False
 Else
      Timer2.Enabled = True
      For Each MyOutage In colOutages
           rsTemp.FindFirst "MAPNUM = '" & MyOutage.Location & "'"
           If rsTemp.NoMatch = True Then
                RemoveOutage MyOutage
                colOutages.Remove MyOutage.Location
           End If
      Next
 End If
 If cmdView.Caption = "Click to View Buckets" Then
      TreeView1(0).Visible = True
      If TreeView1(1).Nodes.Count > 0 Then
           cmdView.Enabled = True
           ClearBuckets
           InsertBuckets
           HideBuckets
      Else
           cmdView.Enabled = False
      End If
 Else
           TreeView1(1).Visible = True
           ClearBuckets
           InsertBuckets
           ShowBuckets
      Else
      End If
 End If
Exit_Here:
 Exit Sub
Err_Control:
 Select Case Err.Number
      Case Else
           LogError Err.Number, Err.Description, "UpdateOutages", "OutageTree.ctl"
           Resume Next
 End Select
Private Function AddOutageToCollection(Outage As clsOutageLocation, col As Collection) As Boolean
Dim bKeyExists As Boolean
Dim tempOutage As clsOutageLocation
On Error GoTo addOutageToCollection_Error
 bKeyExists = False
 col.Add Outage, Outage.Location  '<=set the key so it is easy to find the outage
 If bKeyExists = False Then
      'Add to Treeview and Blocks
      If Outage.Bucket <> "" Then
           'Propably need to Add the Blocks in the AddNodeToTree Sub
           AddNodeToTree 1, Outage.Bucket, Outage.Device, Outage.Location, Outage
      Else
           AddNodeToTree 0, Outage.SubCir, Outage.Device, Outage.Location, Outage
      End If
 Else
      Set tempOutage = col.Item(Outage.Location)
      If tempOutage.Bucket <> Outage.Bucket Then
           'delete the old outage in the tree add it to the correct tree and bucket
           RemoveOutage tempOutage
           tempOutage.Bucket = Outage.Bucket
           tempOutage.Device = Outage.Device
           tempOutage.SubCir = Outage.SubCir
           If tempOutage.Bucket <> "" Then
                AddNodeToTree 1, tempOutage.Bucket, tempOutage.Device, tempOutage.Location, Outage
           Else
                AddNodeToTree 0, tempOutage.SubCir, tempOutage.Device, tempOutage.Location, Outage
           End If
      End If
 End If
ExitHere:
    bKeyExists = False
    On Error GoTo 0
    Exit Function
addOutageToCollection_Error:
    Case 457 'the key already exists
        bKeyExists = True
        Resume Next
    Case Else
        LogError Err.Number, Err.Description, "AddOutageToCollection", "OutageTree.ctl"
        Resume ExitHere
    End Select
End Function
Private Sub AddNodeToTree(intTreeIndex As Integer, strSC As String, strDev As String, strLoc As String, Outage As clsOutageLocation)
Dim strBucketKey As String
Dim strDeviceKey As String
Dim strLocKey As String
Dim bKeyExist As Boolean
Dim varInsPnt As Variant
Dim strLocList As String
Dim strAttValue As String
Dim strType As String
Dim strHandle As String
Dim blnTreeVisible As Boolean
 strBucketKey = strSC
 strDeviceKey = strSC & strDev
 strLocKey = Outage.Location
 'Add Sub-Cir
 TreeView1(intTreeIndex).Nodes.Add Key:=strBucketKey, Text:=strSC
 Set nd = TreeView1(intTreeIndex).Nodes(strBucketKey)
 nd.Tag = "SCS"
 If bKeyExist = False Then
      'Add The Block if it is a bucket
'           If GetCenter(Outage.Bucket, varInsPnt) = True Then
'                AddBlocks varInsPnt, "OutageCalls", "Flag", Outage.Bucket, Outage.Bucket
'           End If
      Else
           nd.Expanded = True
      End If
 End If
 bKeyExist = False
 'Add Device
 TreeView1(intTreeIndex).Nodes.Add strSC, tvwChild, strDeviceKey, strDev
 Set nd = TreeView1(intTreeIndex).Nodes(strDeviceKey)
 nd.Tag = "DEV"
      If Outage.Bucket = "" Then
           nd.Expanded = True
      End If
      'Add The Block
      strLocList = "Select * from SSMap WHERE [Location] LIKE '*" & strDev & "*'"
      strAttValue = strDev
      If InStr(2, strDev, "RC") > 2 Then
           strType = "RC"
      ElseIf InStr(2, strDev, "FU") > 2 Then
           strType = "FU"
      Else
           strType = ""
      End If
      If strType <> "" Then
           Set rsSSTemp = OpenRSSSMap(strLocList)
           If rsSSTemp.BOF = False Or rsSSTemp.EOF = False Then
                rsSSTemp.MoveFirst
                strHandle = rsSSTemp.Fields("Handle")
                AddBlocks HandleToInsertionPoint(strHandle), "OutageCalls", strType, strAttValue, strSC
           End If
      End If
 End If
 bKeyExist = False
 'Add Location
 TreeView1(intTreeIndex).Nodes.Add strSC & strDev, tvwChild, strLocKey, strLoc
 Set nd = TreeView1(intTreeIndex).Nodes(strLocKey)
 nd.Tag = "LOC"
           nd.Expanded = True
      End If
      'Add The Block
      strLocList = "Select * from SSMap WHERE [Location] LIKE '*" & strLoc & "*'"
      strAttValue = strLoc
      strType = "SER"
           rsSSTemp.MoveFirst
      End If
 End If
 bKeyExist = False
Exit_Here:
 Exit Sub
Err_Control:
      Case 35602
           'Duplicate key is not unique
           bKeyExist = True
           Err.Clear
           Resume Next
     Case Else
           LogError Err.Number, Err.Description, "AddNodeToTree", "OutageTree.ctl"
           Resume Exit_Here
 End Select
Sub RemoveOutage(Outage As clsOutageLocation)
 'Remove From Treeview Here and Blocks
      Set ndLocation = TreeView1(1).Nodes(Outage.Location)
      Set ndDevice = ndLocation.Parent
      If ndDevice.Children = 1 Then
           Set ndBucket = ndDevice.Parent
           If ndBucket.Children = 1 Then
                'Remove Bucket,Device, & Location
                RemoveBucket Outage.Bucket
                RemoveDevice Outage.Device
                RemoveLocation Outage.Location
                TreeDeleteSection 1, ndBucket
           Else
                'Remove Device & Location
                TreeDeleteSection 1, ndDevice
           End If
      Else
           'Remove Location
           TreeDeleteSection 1, ndLocation
      End If
 Else
      Set ndLocation = TreeView1(0).Nodes(Outage.Location)
                TreeDeleteSection 0, ndBucket
           Else
                TreeDeleteSection 0, ndDevice
           End If
      Else
           'Remove Location
           TreeDeleteSection 0, ndLocation
      End If
 End If
Exit_Here:
 Exit Sub
Err_Control:
      Case Else
           LogError Err.Number, Err.Description, "RemoveOutage", "OutageTree.ctl"
           Resume Next
 End Select
« Last Edit: February 27, 2006, 01:58:04 PM by ChuckHardin »
ChuckHardin
« Reply #2 on: February 27, 2006, 01:38:07 PM »
Here is most the code for toggling between treeviews
Private Sub cmdView_Click()
 'Toggles between the treeviews
 Select Case cmdView.Caption
      Case "Click to View Buckets"
           TreeView1(0).Visible = False
           ToggleTrees 0
           cmdView.Caption = "Click to View Unassigned"
      Case "Click to View Unassigned"
           TreeView1(1).Visible = False
           ToggleTrees 1
 End Select
Public Sub ToggleTrees(intTreeToShow As Integer)
Dim BucketsOn As Boolean
Dim NodeX As MSComctlLib.Node
Dim intNodecnt As Integer
 'Maybe do this for each tree
 'Then For each node.parent is nothing
 'Show or Hide blocks by node.text
 For intcnt = 0 To 1
      If TreeView1(intcnt).Nodes.Count > 0 Then
           For intNodecnt = 1 To TreeView1(intcnt).Nodes.Count
                Set NodeX = TreeView1(intcnt).Nodes(intNodecnt)
                If NodeX.Parent Is Nothing Then
                     If intTreeToShow = intcnt Then
                          'Show the blocks
                          If intTreeToShow = 0 Then
                               ShowBlocks NodeX.Text
                          Else
                               If NodeX.Expanded = True Then
                                    'Show the Locations & Devices
                               Else
                                    'Hide the Locations & Devices
                                    HideBlocks NodeX.Text
                               End If
                          End If
                     Else
                          'Hide the Blocks
                     End If
                End If
           Next
      End If
 Next
      HideBuckets
 End If
' Another way I tried it that was not fast enough
' If intTreeToShow = 1 Then BucketsOn = True
' For Each MyOutage In colOutages
'      If MyOutage.Bucket = "" Then
'           If BucketsOn Then
'                'Hide These
'                HideBlocks MyOutage.SubCir
'           Else
'                'Show These
'                Set NodeX = TreeView1(0).Nodes(MyOutage.SubCir)
'                If NodeX.Expanded = True Then
'                     'Hide the bucket show the Locations & Devices
'                     ShowBlocks MyOutage.SubCir
'                Else
'                     'Show the Bucket hide the Locations & Devices
'                End If
'           End If
'      Else
'           If BucketsOn Then
'                'Show These
'                Set NodeX = TreeView1(0).Nodes(MyOutage.Bucket)
'                     'Show the Locations & Devices
'                     ShowBlocks MyOutage.Bucket
'                Else
'                     'Hide the Locations & Devices
'                     HideBlocks MyOutage.Bucket
'                End If
'           Else
'                'Hide These
'           End If
'      End If
' Next
ExitHere:
 Exit Sub
Err_Control:
      Case Else
           Resume ExitHere
 End Select
Public Function HideBlocks(strBucket As String) As Boolean
Dim objSelSet As AcadSelectionSet
Dim objEnt As AcadEntity
Dim objBlkRef As AcadBlockReference
Dim intType(0 To 1) As Integer
Dim varData(0 To 1) As Variant
Dim varAtts As Variant
Dim objAttRef As AcadAttributeReference
Dim intLoop As Integer
 Set objSelSet = Thisdrawing.PickfirstSelectionSet
 intType(0) = 0: varData(0) = "INSERT"
 intType(1) = 2: varData(1) = BlockAttributeFilter("BUCKET")
 objSelSet.Select Mode:=acSelectionSetAll, FilterType:=intType, FilterData:=varData
 For Each objEnt In objSelSet
      If TypeOf objEnt Is AcadBlockReference Then
           Set objBlkRef = objEnt
           If objBlkRef.HasAttributes Then
                varAtts = objBlkRef.GetAttributes
                For intLoop = LBound(varAtts) To UBound(varAtts)
                     Set objAttRef = varAtts(intLoop)
                     If objAttRef.TagString = "BUCKET" Then
                          If strBucket = objAttRef.TextString Then
                               If objBlkRef.Name = "Flag" Then
                                    objBlkRef.Visible = True
                               Else
                                    objBlkRef.Visible = False
                               End If
                          End If
                     End If
                Next intLoop
           End If
      End If
 Next
 ACADApp.Update
 Set objSelSet = Nothing
 Set objEnt = Nothing
 Set objBlkRef = Nothing
 HideBlocks = True
Exit_Here:
 Exit Function
Err_Control:
      Case Else
           LogError Err.Number, Err.Description, "HideBlocks", "modACAD.bas"
           HideBlocks = False
           Resume Exit_Here
 End Select
End Function
Public Function ShowBlocks(strBucket As String) As Boolean
Dim interr As Integer
                               Else
                               End If
                          End If
                     End If
                Next intLoop
           End If
      End If
 Next
 ACADApp.Update
 ShowBlocks = True
Exit_Here:
 Exit Function
Err_Control:
      Case Else
           ShowBlocks = False
           Resume Exit_Here
 End Select
End Function
Public Function HideBuckets() As Boolean
 intType(1) = 2: varData(1) = "Flag"
           End If
      End If
 Next
 ACADApp.Update
 HideBuckets = True
Exit_Here:
 Exit Function
Err_Control:
      Case Else
           LogError Err.Number, Err.Description, "HideBuckets", "modACAD.bas"
           HideBuckets = False
           Resume Exit_Here
 End Select
End Function
Public Function ShowBuckets() As Boolean
           End If
      End If
 Next
 ACADApp.Update
 ShowBuckets = True
Exit_Here:
 Exit Function
Err_Control:
      Case Else
           LogError Err.Number, Err.Description, "ShowBuckets", "modACAD.bas"
           ShowBuckets = False
           Resume Exit_Here
 End Select
End Function
fxcastil
« Reply #3 on: February 27, 2006, 06:36:37 PM »
Chuck,
I have used the tree view a few times and have found it to be quite slow for large data base.
A simple list box would be much faster if you can use that instead.
Another thing to avoid is using a for/next or do/while loop to read a database.  Instead transfer the database to an Array in VBA this will be much faster.
also change
to
For Each objBlockReference In objSelSet  ' since you selection set is already blocks references "Inserts"
Have you tested the code to see where your longest delay is ?
Fred Castillo
Bryco
« Reply #4 on: February 28, 2006, 02:00:28 AM »
Hi Chuck. Man that's a good sized dwg.
I was wondering if you put a timer on  the  blockrefs part, if that would be longer than the rest.
If so, perhaps this dwg has a finite qty of blockrefs, in which case you could make a collection of integers (eg modelspace(20077)) to represent the blockrefs and work w/ that. (Like making a class for the dwg.)
intType(1) = 2: varData(1) = BlockAttributeFilter("BUCKET") ->sounds slow
 For intLoop = LBound(varAtts) To UBound(varAtts)-> if the blockrefs are constant use varAtts(number)
There's no exit for (maybe there is only 2 atts)
Jürg Menzi
  • Oberegg, Switzerland
« Reply #5 on: February 28, 2006, 02:58:13 AM »
Chuck
To increase the speed while filling a tree view, we do following:
First, just fill the parent level w/o any child levels. Fill the child level on open the selected node.
A computer's human touch is its unscrupulousness!
MENZI ENGINEERING GmbH
Current A2k16... A2k24 - Start R2.18
ChuckHardin
« Reply #6 on: February 28, 2006, 09:30:18 AM »
If you do for each objblkref in objselset you can get an annoying error on next objblkref
when filling the tree I have records that come in that have a format of:
MapNumber    Device    Sub    Circuit     Bucket      Status
So the easiest is to just try to add the node and catch the error
If you turn the treeview visible to false for adding nodes it is fast
there are only 2 atts Bucket and Outage
I think I came up the solution last night
When I create the node and insert the block I need to save the handle to the tag value of the node
Root Node  Tag = SCS|handle
Device Node Tag = DEV|handle
Call In Node Tag = LOC|handle
then just do a for each node in treeview
  set objent = thisdrawing.HandleToObject(right(Tag,len(tag)-4))
  objent.visible = True/False
The search of blocks is what takes so long
It has to search through the same set of blocks every time it hits a new root node.
this way I am only dealing with the blockref for the correct nodes
NO MORE SEARCHING YAAAAAA  :-D
Thanks everyone for the replies. I'll let yall know how it functions later.
Jürg Menzi
« Reply #7 on: February 28, 2006, 09:43:04 AM »
Chuck
One last remark for the moment:
Keep in mind that the tree control has a limit of 32'767 nodes
ChuckHardin
« Reply #8 on: February 28, 2006, 09:48:25 AM »
Crap!!
Well hopefully with 2 treeviews I'll be alright.
Guess I need to check out the vbaccelerator treeview control.
ChuckHardin
« Reply #9 on: March 09, 2006, 12:15:05 AM »
All issues were worked out to everyones satisfaction.
The speed is great. We tested it with 1000 calls.
About 2000 nodes in the tree views. No problems!!
I changed all block subs and functions to use
Thisdrawing.HandleToObject
Also Check RsTemp.Fields("Location") with OutageCollection
Add If Key doesn't exist
Then For each Outage FindFirst MyOutage.Location
Remove MyOutage if noMatch=True
They love the app now!!!
Thanks yall
Jürg Menzi
« Reply #10 on: March 09, 2006, 02:45:55 AM »
That's a clipping from one of my works using the tree control (Master data rail switch database). Because of more
than 60'000 datasets, the sub's are filled while click on the node:
ChuckHardin
« Reply #11 on: March 09, 2006, 02:43:23 PM »
Cool we will have to check into it some more when things slow down.