Author Topic: Help with a Commercial Plan Notes?  (Read 10303 times)
« on: June 12, 2007, 08:48:06 PM »
I'm trying to read some ragged reduced size prints and usually only deal with houses.
This plan is a 2 story office building.
What size is an 'I' beam when the call out is 'W18x50'  'W18x40' 'W18x31'
How about a Bar Joist '14H3'  '8H3'
And how would one call out a concrete foundation pad with 2 layers of steel?
16'-0" x 3'-0" x 1'-6" With 9 #4 rebar the short direction & 4 #5 rebar in the long direction, #5 on the bottom
What is you wanted two rebar mats, one on top of the pad & one bottom?
Peter Laker
Re: Help with a Commercial Plan Notes?
« Reply #1 on: June 12, 2007, 09:38:55 PM »
Can help you with the I Beams.
These are American imperial I sections
W18x50
Mass=74.4
D=457.2
B=190.5
T=14.29
t=9.53
r=17.46
W18x40
Mass=59.52
D=454.02
B=152.40
T=12.70
t=7.94
r=17.46
no W18x30 in my tables
SMALLEST IS W18x35
Mass=52.08
D=450.85
B=152.40
T=11.11
t=7.94
r=17.46
« Reply #2 on: June 13, 2007, 12:20:27 AM »
Thanks Peter and welcome to theSwamp. :-)
« Reply #3 on: June 13, 2007, 12:40:27 AM »
Hello Peter,
Good to hear from you.
Are you exporting your talents these days ??
regards
kwb
« Reply #4 on: June 13, 2007, 01:31:57 PM »
CAB,
I looked at my charts and I have different numbers than Peter ... although I do not have W18x31 either ...
the smallest I have is W18x35 ...
anyway ...
W18x40
width = 6.015
height = 17.90
W18x50
width = 7.495
height = 17.99
8H3 and 14H3 seem to be designations for open web steel trusses. If that is the case the height is 8 and 14 respectively. I don't have anything indicating the width of the trusses.
deegeecees
« Reply #5 on: June 13, 2007, 01:48:03 PM »
If all you need is relative sizes, then DDSTEEL.LSP has W4x13 thru W36X300.
Josh Nieman
« Reply #6 on: June 13, 2007, 02:04:36 PM »
There's a W8X31... common common beam... maybe a typo made it 18?
Bob Garner
« Reply #7 on: June 13, 2007, 02:19:42 PM »
Slab rebar callout:
Top Steel: 9-#4 longitudinal, 4-#5 transverse
Bottom Steel: 4-#5 etc., etc.
Or 9-#4 longitudinal, 4-#5 transverse, top and bottom
With or without leaders pointing to the reinf.
There's other ways, too.  Anything that communicates to the rod-busters.
Bob
Bob Garner
« Reply #8 on: June 13, 2007, 02:21:22 PM »
Whoops, I transposed the bar quantities for the longitudinal vs. transverse bars.
Sorry.
B
« Reply #9 on: June 13, 2007, 06:29:38 PM »
Thanks Bob, that helps.
« Reply #10 on: June 13, 2007, 06:30:30 PM »
I should have thought of that. I do have that lisp.
« Reply #11 on: June 13, 2007, 06:32:24 PM »
Yes, I now think that it is a typo.
I think it reads  W16x31
Thanks Josh and Keith
Peter Laker
« Reply #12 on: June 19, 2007, 08:54:34 PM »
Hi Kerry,
No haven't done any contract work for 4 years now, just been working full time (wages) on the sunny coast & enjoying the weather.
Have been looking at getting into a bit of coding again though, been reading up on C#, looks much easier than C & C++.
Cheers...
Pete